out here, thinkin its NEC anyways, you must bond:
gas main, water main , and structure (if steel building) in 1 continuous unbroken line to the panel. this eliminates the static charge from the gas main as well. in this dwelling, afore, the gas main was 6ft away, and the water main is 100ft away..I was told with the gas so close, they could get away with a seperate bond to each.
as for ground rods...here in Maricopa county (AZ) we are required to drive 2 5/8" x 8' ground rods with a 6ft min seperation at the service section (commercial)or panel (residential). you must also bond the water , gas, and steel structure to the panel as well.
They do like to see a ufer bond (#4 solid tied to rebar for 25' in concrete foundation) connected to the panel along with the others.
with the arrid desert here, we have no BOND until it rains...
I will check the NEC..pretty sure most , if not all of that is in there...then of course each municipality can have its own more strict ordinances pertaining to construction installation...
out here, thinkin its NEC anyways, you must bond:
gas main, water main , and structure (if steel building) in 1 continuous unbroken line to the panel. this eliminates the static charge from the gas main as well. in this dwelling, afore, the gas main was 6ft away, and the water main is 100ft away..I was told with the gas so close, they could get away with a seperate bond to each.
as for ground rods...here in Maricopa county (AZ) we are required to drive 2 5/8" x 8' ground rods with a 6ft min seperation at the service section (commercial)or panel (residential). you must also bond the water , gas, and steel structure to the panel as well.
They do like to see a ufer bond (#4 solid tied to rebar for 25' in concrete foundation) connected to the panel along with the others.
with the arrid desert here, we have no BOND until it rains...
I will check the NEC..pretty sure most , if not all of that is in there...then of course each municipality can have its own more strict ordinances pertaining to construction installation...
#24
![Default](https://dodgeforum.com/forum/images/icons/icon1.gif)
ORIGINAL: bajafun
out here in the desert, the panels are mounted on the outside of the dwellings. since our average rain fall is not enough to fill a circle k 44oz thirst buster cup..its ok ![Wink](https://dodgeforum.com/forum/images/smilies/wink.gif)
ORIGINAL: 07 Ram TRX4
The circuit breaker should be "IN THE HOUSE"... Not on it....
The circuit breaker should be "IN THE HOUSE"... Not on it....
![Wink](https://dodgeforum.com/forum/images/smilies/wink.gif)
#25
![Default](https://dodgeforum.com/forum/images/icons/icon1.gif)
ORIGINAL: sharx ram
You tell um Tiger... [8D] Its refreshing to hear someone who knows what thier talking about!!!
ORIGINAL: bajafun
out here, thinkin its NEC anyways, you must bond:
gas main, water main , and structure (if steel building) in 1 continuous unbroken line to the panel. this eliminates the static charge from the gas main as well. in this dwelling, afore, the gas main was 6ft away, and the water main is 100ft away..I was told with the gas so close, they could get away with a seperate bond to each.
as for ground rods...here in Maricopa county (AZ) we are required to drive 2 5/8" x 8' ground rods with a 6ft min seperation at the service section (commercial)or panel (residential). you must also bond the water , gas, and steel structure to the panel as well.
They do like to see a ufer bond (#4 solid tied to rebar for 25' in concrete foundation) connected to the panel along with the others.
with the arrid desert here, we have no BOND until it rains...
I will check the NEC..pretty sure most , if not all of that is in there...then of course each municipality can have its own more strict ordinances pertaining to construction installation...
out here, thinkin its NEC anyways, you must bond:
gas main, water main , and structure (if steel building) in 1 continuous unbroken line to the panel. this eliminates the static charge from the gas main as well. in this dwelling, afore, the gas main was 6ft away, and the water main is 100ft away..I was told with the gas so close, they could get away with a seperate bond to each.
as for ground rods...here in Maricopa county (AZ) we are required to drive 2 5/8" x 8' ground rods with a 6ft min seperation at the service section (commercial)or panel (residential). you must also bond the water , gas, and steel structure to the panel as well.
They do like to see a ufer bond (#4 solid tied to rebar for 25' in concrete foundation) connected to the panel along with the others.
with the arrid desert here, we have no BOND until it rains...
I will check the NEC..pretty sure most , if not all of that is in there...then of course each municipality can have its own more strict ordinances pertaining to construction installation...
I need to pick me up a copy of the illustrated NEC ..it runs $125 an issue [:@]
Sharky..what juristiction do you cover?
#27
![Default](https://dodgeforum.com/forum/images/icons/icon1.gif)
triton...wuts with the parallel feed?
Im still lookin at it..
I dont agree with the splice blocks in the gutter..wuts with the ground and netrals on the same terminal???
whats Sharky got to say???
I have to look more....had to make the pic bigger since Im not there!!!
Im still lookin at it..
I dont agree with the splice blocks in the gutter..wuts with the ground and netrals on the same terminal???
whats Sharky got to say???
I have to look more....had to make the pic bigger since Im not there!!!
#28
![Default](https://dodgeforum.com/forum/images/icons/icon1.gif)
ORIGINAL: bajafun
wasI wrong?
I need to pick me up a copy of the illustrated NEC ..it runs $125 an issue [:@]
Sharky..what juristiction do you cover?
ORIGINAL: sharx ram
You tell um Tiger... [8D] Its refreshing to hear someone who knows what thier talking about!!!
ORIGINAL: bajafun
out here, thinkin its NEC anyways, you must bond:
gas main, water main , and structure (if steel building) in 1 continuous unbroken line to the panel. this eliminates the static charge from the gas main as well. in this dwelling, afore, the gas main was 6ft away, and the water main is 100ft away..I was told with the gas so close, they could get away with a seperate bond to each.
as for ground rods...here in Maricopa county (AZ) we are required to drive 2 5/8" x 8' ground rods with a 6ft min seperation at the service section (commercial)or panel (residential). you must also bond the water , gas, and steel structure to the panel as well.
They do like to see a ufer bond (#4 solid tied to rebar for 25' in concrete foundation) connected to the panel along with the others.
with the arrid desert here, we have no BOND until it rains...
I will check the NEC..pretty sure most , if not all of that is in there...then of course each municipality can have its own more strict ordinances pertaining to construction installation...
out here, thinkin its NEC anyways, you must bond:
gas main, water main , and structure (if steel building) in 1 continuous unbroken line to the panel. this eliminates the static charge from the gas main as well. in this dwelling, afore, the gas main was 6ft away, and the water main is 100ft away..I was told with the gas so close, they could get away with a seperate bond to each.
as for ground rods...here in Maricopa county (AZ) we are required to drive 2 5/8" x 8' ground rods with a 6ft min seperation at the service section (commercial)or panel (residential). you must also bond the water , gas, and steel structure to the panel as well.
They do like to see a ufer bond (#4 solid tied to rebar for 25' in concrete foundation) connected to the panel along with the others.
with the arrid desert here, we have no BOND until it rains...
I will check the NEC..pretty sure most , if not all of that is in there...then of course each municipality can have its own more strict ordinances pertaining to construction installation...
I need to pick me up a copy of the illustrated NEC ..it runs $125 an issue [:@]
Sharky..what juristiction do you cover?
I work in the town ofWickenburg.
#29
![Default](https://dodgeforum.com/forum/images/icons/icon1.gif)
ORIGINAL: sharx ram
You nailed it right on the head with the exception, it 20 feet in the concrete not 25, but over kill is always better [8D]
I work in the town ofWickenburg.
ORIGINAL: bajafun
wasI wrong?
I need to pick me up a copy of the illustrated NEC ..it runs $125 an issue [:@]
Sharky..what juristiction do you cover?
ORIGINAL: sharx ram
You tell um Tiger... [8D] Its refreshing to hear someone who knows what thier talking about!!!
ORIGINAL: bajafun
out here, thinkin its NEC anyways, you must bond:
gas main, water main , and structure (if steel building) in 1 continuous unbroken line to the panel. this eliminates the static charge from the gas main as well. in this dwelling, afore, the gas main was 6ft away, and the water main is 100ft away..I was told with the gas so close, they could get away with a seperate bond to each.
as for ground rods...here in Maricopa county (AZ) we are required to drive 2 5/8" x 8' ground rods with a 6ft min seperation at the service section (commercial)or panel (residential). you must also bond the water , gas, and steel structure to the panel as well.
They do like to see a ufer bond (#4 solid tied to rebar for 25' in concrete foundation) connected to the panel along with the others.
with the arrid desert here, we have no BOND until it rains...
I will check the NEC..pretty sure most , if not all of that is in there...then of course each municipality can have its own more strict ordinances pertaining to construction installation...
out here, thinkin its NEC anyways, you must bond:
gas main, water main , and structure (if steel building) in 1 continuous unbroken line to the panel. this eliminates the static charge from the gas main as well. in this dwelling, afore, the gas main was 6ft away, and the water main is 100ft away..I was told with the gas so close, they could get away with a seperate bond to each.
as for ground rods...here in Maricopa county (AZ) we are required to drive 2 5/8" x 8' ground rods with a 6ft min seperation at the service section (commercial)or panel (residential). you must also bond the water , gas, and steel structure to the panel as well.
They do like to see a ufer bond (#4 solid tied to rebar for 25' in concrete foundation) connected to the panel along with the others.
with the arrid desert here, we have no BOND until it rains...
I will check the NEC..pretty sure most , if not all of that is in there...then of course each municipality can have its own more strict ordinances pertaining to construction installation...
I need to pick me up a copy of the illustrated NEC ..it runs $125 an issue [:@]
Sharky..what juristiction do you cover?
I work in the town ofWickenburg.
Wickenburg?? you not good enough for Phoenix?!?!?!?!
![Big Grin](https://dodgeforum.com/forum/images/smilies/biggrin.gif)
thanks for the compliment up there ^
![Wink](https://dodgeforum.com/forum/images/smilies/wink.gif)
#30
![Default](https://dodgeforum.com/forum/images/icons/icon1.gif)
ORIGINAL: bajafun
triton...wuts with the parallel feed?
Im still lookin at it..
I dont agree with the splice blocks in the gutter..wuts with the ground and netrals on the same terminal???
whats Sharky got to say???
I have to look more....had to make the pic bigger since Im not there!!!
triton...wuts with the parallel feed?
Im still lookin at it..
I dont agree with the splice blocks in the gutter..wuts with the ground and netrals on the same terminal???
whats Sharky got to say???
I have to look more....had to make the pic bigger since Im not there!!!